Site Plan Review Process
Adopted
by the South Lyon Planning Commission
March
24, 1988
Revised-July
14, 1989
Revised-July
20, 2001
To all persons seeking site plan approval before the South Lyon Planning Commission, the following procedure shall apply:
Site
plans shall be submitted as required in the South Lyon Zoning Ordinance and
shall be prepared in accordance with the site plan review requirements of the
zoning ordinance and this document.
An applicant seeking site plan approval shall first obtain a copy of the South Lyon Zoning Ordinance, Zoning Map and a copy of this document. The applicant should acquaint themselves with the applicable requirements and site plan processing format contained therein to make sure that:
The
site is properly zoned to support the use proposed for development.
The building, height, bulk, density, area, off-street parking, landscaping and screening requirements are met.
Once
an applicant is certain that the site is properly zoned and that the site plan
is properly prepared, the applicant shall sign the attached checklist, detach it
from this document and submit it, along with seventeen (17) FOLDED copies
of the site plan to Planning Commission Coordinator for processing.
The
Planning Commission Coordinator shall collect the application fee as established
by City Council before processing any site plan. Upon collection of applicable
fees the site plan will be forwarded with a letter of transmittal to all
assigned review agencies set forth below.
Building
Department
One (1) copy
DPW Superintendent
One (1) copy
Police
Department
One (1) copy
Fire
Departments
One (1) copy
Planning
Consultant
Two (2) copies
Engineering
Consultant
Two (2) copies
Planning
Commissioners
Nine
(9) copies
The above review agencies, upon receipt of site plans from the City, shall review the site plan for compliance with applicable City codes and ordinances and forward their review comments in writing, to the Planning Commission Coordinator within twenty (20) working days. Upon request of the applicant,
copies of
the review agencies comments shall be made available, after receipt of the
comments by the City.
If
all review agency comments are positive and no concerns are expressed relative
to the site plan, the Planning Commission Coordinator shall notify the applicant
and schedule the site plan for review by the Planning Commission no later than five
(5) working days prior to the next scheduled meeting.
If any designated review agency comments note concern or problems with the site plan, the City shall not schedule the site plan for review by the Planning Commission. Except in those instances where the applicant is aware that problems exist with the site plan and seeks site plan denial by the Planning
Commission in order to gain access to
the Zoning Board of Appeals.
If
problems are found by the reviewing agencies to exist with a site plan and the
applicant does not wish to seek relief from the Zoning Board of Appeals, the
applicant shall prepare revised site plans containing all modifications set
forth in the review agency comments. Seventeen (17) of the FOLDED
revised site plans shall be submitted to the City by the applicant to permit
re-distribution to all review agencies.
Revised
site plans shall be submitted to the Planning Commission Coordinator for
referral to the review agencies in the same manner as followed for initial site
plan review.
Again,
upon request of the applicant, copies of the review agencies comments shall be
made available, after receipt of the comments by the City.
The same procedure shall be followed for all subsequent revised site
plans until all concerns expressed by the review agencies are satisfactorily
resolved, only then shall the Planning Commission Coordinator schedule the site
plan review by the Planning Commission in accordance with the minimum five
(5) workdays scheduling procedure set forth above.
At
the meeting, the Planning Commission shall review the site plan and will take
one of the following courses of action:
Approve
the site plan
Table
approval of the site plan
Disapprove
the site plan
Approval
of a site plan may be granted by a simple majority of a lawful quorum of the
Planning Commission members in attendance. A stamped approved site plan with
date of approval will be forwarded to the applicant with a letter of transmittal
noting the approval.
If
a site plan is tabled for further review, the Planning Commission will so note
its reason(s) for such action. Absence of the applicant or any representative in
place of the applicant, at a scheduled review of the site plan by the Planning
Commission, may be grounds for tabling the site plan. If a site plan is
disapproved, the Planning Commission will note the reason(s) for disapproval and
will return the site plan to the Planning Commission Coordinator.
A
site plan disapproved by the Planning Commission will be:
Revised
and resubmitted for further review,
Scheduled
for action by the Zoning Board of Appeals, or
Removed
by the applicant from further consideration
A
site plan disapproved by the Planning Commission will not be rescheduled for
review by the Commission until the area(s) of concern noted in its disapproval
have been satisfactorily resolved by:
Submittal
of a revised site plan
A
favorable resolution of the problems by the Zoning Board of Appeals
Approval
of a site plan by the Planning Commission will be in effect for a period of one
(1) year from date of approval of the site plan. One (1) year site plan approval
extensions may be granted by the Planning Commission upon review of a written
request by the applicant documenting the reasons for an extension.
Revisions
to an approved site plan, requested by an applicant, will be processed in the
same manner as set forth herein for an initial site plan review.
The
following site plan review checklists are provided for use by the applicant
preparing a site plan for submittal and by the designated review agencies in
making their review.
A site plan submitted for review and approval by the Planning Commission shall not be accepted unless the appropriate checklist has been reviewed by the applicant, the same's signature has been affixed to the checklist in the place provided for it, and the review fee paid.
During
the course of preparing a site plan, the applicant may call the following
designated review agencies for assistance in interpreting the applicable
standards of the Zoning Ordinance and the requirements of the document.
South
Lyon Building Inspector
248-437-5255
Police
Department
248-437-1773
Fire
Department
248-437-2616
DPW
Director
248-437-4006
Planning
Commission Coordinator
248-437-1735
City
of South Lyon
The
Following, To Be Completed By Applicant Prior To Submittal Of Site Plan:
Developers
Name _________________________________________________
Address
____________________________________________________
Phone Number
____________________________________________________
Legal
Property Owner ________________________________________________
Address
____________________________________________________
Phone Number
____________________________________________________
Site
Plan Designers __________________________________________________
Name
______________________________________________________
Address
____________________________________________________
Phone Number
_______________________________________________
Registration
Number __________________________________________
Description
of Proposed Development: ________ New ________ Addition
If an appeal of the strict application of the standards of the Zoning Ordinance is to be taken, please so indicate below.
Appeal
Requested_______________________________________________________
For City Use Only:
Initial Site Plan Review fee paid
(date)_______________________________________________
Site Plan Application
Number_____________________________________________
Purchase Order Number
________________________________________________
____________________________________________________Residential
Site Plan
Prior
to submittal of a site plan, the applicant shall review the following elements
for inclusion, where applicable, on the site plan, and shall be in sufficient
detail to meet the intent and purpose of the review process. The applicant will
check the box in the left hand column marked 'Applicant' only and will mark all
applicable elements. A check mark by the applicant for each element involved
will indicate that the applicant made the proper notation on the site plan. If
the applicant is satisfied that all such information required is properly noted
on the site plan, the applicant will sign and date the checklist in the place
provided and submit the signed Site Plan Review Application Form with the site plan to the Planning Commission Coordinator. The applicant will check only the
column marked 'Applicant'.
Checked
by Checked
by
Applicant
Review Agency
Name
of Development
___________ ___________
Name,
address & phone number of:
Developer
___________ __________
Legal
Owner
___________ __________
Designer/Firm
___________ __________
Designer
Registration No. and Seal
___________ __________
Scale
of Drawing
If
less than 3 acres- 1” = 50'
___________ __________
If
more than 3 acres 1" = 100'
___________ __________
Sheet
size shall not exceed 24" x 36”
___________ __________
Legend
___________ __________
Date
___________ __________
North
Point
___________ __________
Complete legal description of entire site i.e. Metes & Bounds description if acreage Parcel,
lot #(s) and subdivision name. All Legal descriptions will
include:
Gross
# of acres
___________ __________
Net
usable acres
___________ __________
Section
Number
___________ __________
Checked by Checked by
Applicant
Review Agency
Vicinity
Sketch or Site Map which does
not
have to be drawn to scale
___________ __________
Topographic
elevations at 10 foot intervals
on and off the site
Existing
___________
__________
Proposed
___________
__________
Existing
drainage courses and existing lake or
stream elevation's
___________ __________
The
location of all existing & proposed on-site
utilities
including their connection to
off-site
utilities
Water
Supply
Existing
___________ ___________
Proposed
___________ ___________
Sanitary
Sewer Supply
Existing
___________ ___________
Proposed
___________ ___________
Storm
Sewer Supply
Existing
___________ ___________
Proposed
___________ ___________
Electric
Supply (above & below ground)
Existing
___________ ___________
Proposed
___________ ___________
Telephone
Supply (above & below ground)
Existing
___________ ___________
Proposed
___________ ___________
Gas
Supply
Existing
___________ ___________
Proposed
___________ ___________
Other
Existing
___________ __________
Proposed
___________ __________
Existing
Zoning Classification of the parcel
___________ __________
Applicant
Review Agency
Existing
Zoning Classification of adjacent parcels
___________ __________
Existing
land use on adjacent parcels
___________ __________
The
location of all existing buildings
___________ __________
& structures within I00' of parcel
The
location of all building and structures
on
site.
___________ __________
All
building/structure height's
___________ __________
Location
of all off-street parking spaces
including required handicapped spaces,
vehicle maneuvering lanes, and service
drives
___________ ___________
Location
of all loading/unloading facilities
___________ ___________
Location
of all driveways, drives, and
turning lanes
___________ ___________
Location
of all drives, driveways & intersections
across
abutting streets from parcel
___________ ___________
Names,
locations, right-of-way widths,
center-
lines, and pavement widths of all
bordering
roads, streets, and easements
___________ ___________
Location
of all sidewalks
___________ ___________
23.
Critical
site dimensions
Along
property lines
___________
___________
Between
buildings
___________
___________
Between
parking & buildings
___________ ___________
Between
parking & parcel lines
___________
___________
Between
principal & accessory buildings
___________
___________
Parking
space width/length (typical)
___________ ___________
Vehicle
maneuvering lane/service
drive
widths
___________
___________
Curb
radius (entrances)
___________
___________
Between
buildings & parcel lines
___________
___________
Between
buildings &
retention/detention
ponds
___________
___________
Checked
by Checked
by
Applicant
Review Agency
24.
Building
Layouts (typical floor plan) including:
Principal
entrances & service entrances
___________
___________
The
relationship between units within
a
building
___________ ___________
Exterior
building wall facade drawings
of
all exposed walls
___________
___________
Building
elevation drawings showing the type
and color of exterior building wall
facade
materials to be covered by signs to be
attached to the building
___________ ___________
Location,
size & type of signs to be utilized
shall
be provided for the site and building's
on
the site. In instances where signs are not
determined
due to unknown occupants at the
time
of site plan review, it shall be required
that
all signs receive the review and approval
of
the Planning Commission prior to occupancy
of
a structure.
___________ ___________
The
location and extent of any outdoor
storage
areas
___________ ___________
The
type, height & extent of any outdoor
storage
areas
___________ ___________
The
type & height of screening for trash
Receptacles
___________ ___________
The
location type & extent of any required
screening
devices.
___________ ___________
A
complete landscape planting plan identifying
all
landscape plantings by location, type and
height.
Where earth berms are used, their height
and
width shall be noted and a cross section of
the
berm included
___________ ___________
32. The location & type
of all outdoor lighting
___________ ___________
Checked
by Checked
by
Applicant
Review Agency
33.
FOR MULTIPLE
DWELLING DEVELOPMENTS:
The
maximum lot coverage of all buildings
shown
___________ ___________
Formula
for distances between buildings
shown
___________ ___________
Site
density computations including total
number
of dwellings units and number of
bedrooms
per unit. When development is in
phases,
the requirements for b. and c.
above
shall be shown for each phase.
___________ ___________
34.
FOR NON-RESIDENTIAL USES:
a.
Proposed use
___________ ___________
b.
Gross & net usable square feet of floor area
___________ ___________
c.
Seating capacity or maximum occupancy
permitted
___________ ___________
d.
Number of medical examining rooms
dental
chairs, and square footage of
waiting
rooms or beds
___________ __________
e.
Number of employees in largest working
shift
___________ ___________
I hereby certify that I have read and understand the above Checklist items and those items that apply
to my site plan, are included on the
site plan.
Signature
of Applicant: ______________________________________________
Date
Received: ___________________________________________________
Initials
of accepting staff _____________________________________________
Note:
This form should be completed and submitted as part of the site plan for all
facilities.
Name
of business: _________________________________________________________
Name
of business owner: ____________________________________________________
Street
and mailing address: __________________________________________________
Telephone:
_______________________________________________________________
I
affirm that the information
submitted is accurate.
Owner’s
signature: _________________________________________________________
Information
compiled by:____________________________________________________
Part
I- Management of Hazardous Substances and Polluting Materials
1. Y N Will the proposed facility expect to store, use or generate hazardous now or in
the future? If yes, please complete this form and submit with your site
plan.
2.
Y N
Will hazardous substances or polluting materials be reused or recycled
on-site?
3. Y N Will any hazardous substances or polluting materials be stored on-site?
If yes, identify the storage location on the site plan. Describe the size and type
of secondary containment structure here, on an attached page, or as a detail on
the site plan:
___________________________________________________________________
___________________________________________________________________
4. Y N Will new underground storage tanks be located less than 2000 feet from drinking
water wells serving two or more establishments, or less than 300 feet from a single-family
drinking water well?
5. Y N Are existing underground storage tanks on-site less than 200 feet from a drinking
water well serving two or more establishments or less than 50 feet from a single-family
household?
If the answers to #4 or #5 are yes, current or proposed activities may be in violation of State of Michigan
underground storage tank regulations. Michigan Department of Environmental Quality, Environmental
Response Division:
734-953-0241.